Checklist
CHECK LIST FOR QUALITY CONTROL OF RCC WORKS
CHECK LIST FOR QUALITY CONTROL OF RCC WORKS
- Carry out slump test at regular intervals to ensure proper workability.
- While concreting cubes must be taken to as per IS: 456 – 2000 to ensure the quality and strength of concrete by testing at 7, 21, and 28 days.
- Make adequate number of cover blocks & chairs as per the required clear cover of various members. Cover Blocks must be placed at minimum of 1m c/c
- Get reinforcement physical test certificate from supplier/manufacturer.
- Ensure that binding wires are adequately used for tying up of reinforcements.
- Check spacing/length of hooks and overlaps. Laps shall be staggered.
- Check vertical & horizontal alignment & strength of centering and shuttering.
- Ensure that thickness/width of section is adequate for inserting vibrator; else inform the design office for possible revision.
- Ensure proper curing for required number of days. Use curing compound, if member is not easily accessible.
- Check that expansion/construction joints are properly made & at correct location as per the drawings.
- Make proper access/ walking arrangement over slab for proper inspection & to avoid any damage to reinforcements.
- De-bonding compound to shuttering materials.
- Depth and width of all beams must be checked.
- Dimensions, diagonal, plumb and supporting of lift pit should be checked properly.
- All beam sides should be absolutely in line and plumb.
- Over all cleaning should be done before concreting.
- Walk-way Planks to be used while casting the slab.
- Slab concreting should be done in strips (Bays) to avoid cold joints. Concrete should be placed within 30 minutes for next strip otherwise keep the joint alive by putting one/two pans of concrete at joint and vibrate it.
- Spare Vibrator and needless must be kept ready at the place of concreting.
- Concrete should be poured from more than 1 m height to avoid segregation
- Reinforcement should be placed as per specified spacing and diameter