DESIGN OF PILE CAP

pile cap is a thick concrete mat that rests on concrete or timber piles that have been driven into soft or unstable ground to provide a suitable stable foundation. It usually forms part of the foundation of a building, typically a multi-story building, structure or support base for heavy equipment. The cast concrete pile cap distributes the load of the building into the piles. A similar structure to a pile cap is a “raft”, which is a concrete foundation floor resting directly onto soft soil which may be liable to subsidence.

  • As per IS 2911 (Part I/ Sec 3) -2010, the pile cap may be designed by assuming
  • that the load from column is dispersed at 45° from the top of the cap up to the mid
  • depth of the pile cap from the base of the column or pedestal. The reaction from
  • piles may also be taken to be distributed at 45° from the edge of the pile, up to the
  • mid depth of the pile cap. On this basis the maximum bending moment and shear
  • forces should be worked out at critical sections.

ASSUMPTIONS INVOLVED

  • (i) Pile cap is perfectly rigid.
  • (ii) Pile heads are hinged to the pile cap and hence no bending moment is
  • transmitted to piles from pile caps.
  • (iii) Since the piles are short and elastic columns, the deformations and stress distribution are planer.

DESIGN PARAMETERS

  • (i) Shape of pile cap.
  • (ii) Depth of pile cap.
  • (iii) Amount of steel to be provided.
  • (iv) Arrangement of reinforcement.

DESIGN PROCEDURE

  • DETERMINE NUMBER OF PILE
  • PILE CAP ARRANGEMENT AND PLANE DIMENSION
  • PILE CAP PRELIMINARY DEPTH
  • CHECK FORCES IN PILES
  • CHECK FOR PUNCHING SHEAR
  • CHECK FOR SHEAR
  • DESIGN OF MOMENT
  • CHECK FOR BOND
  • DETAILS FOR REINFORCEMENT

Explanation of pile cap design with example:-

EXAMPLE 1 :-

Diameter of pile : 300 mm

Spacing between the piles : 3xd= 3×400 mm      [ As per IS 2911 (Part 1/Sec 3)   :2010 Clause : 6.6.2.]

                                                           = 1200 mm                                                                                               

                                                                                                 

No of piles under a pile cap: 3

Size of column : 400×400 mm

Load transferred by column : 1500 kN

Load on each pile : 1500/3= 500 kN

The dimension of the pile cap, the distance between the connecting line of the piles and the face of critical zone of punching shear are given in the figure with details……….. 

picturn

Details about the pile cap of this example

picture1

We have assume that the effective depth of pile cap is 500 mm………

Unit Moment at face AB = 0.287×1000= 287 kN-m

Unit Moment at face AC = 0.287×1000= 287 kN-m

Unit Moment at face BC = 0.1×1000= 100 kN-m

Formula used to calculate Area of steel against corresponding moment:

Mu= 0.87 x fy x As t x d (1 – 0.42 x Xu/d)

(AS PER IS:456 (2000) ANNEX G , CLAUSE 38.1………

Mu = Moment

fy   = Characteristic strength of steel, here 415

As t  = Area of steel

d= Effective depth of pile cap

Xu= Depth of neutral axis

Area of steel required parallel to AB = 1991 mm2

Area of steel required parallel to AC = 1991 mm2

 

Area of steel required parallel to BC = 693 mm2

  We should provide 12 mm rod of 113 mm2       

  Spacing through AB = (113 x 1000)/1991= 60 mm

Spacing through AC = (113 x 1000)/1991= 60 mm

Spacing through BC = (113 x 1000)/693= 160 mm

OVERALL DEPTH OF THE PILE CAP =(500+(100+12+12+6)X2)= 760 mm

Related Articles

Leave a Reply

Your email address will not be published. Required fields are marked *

Back to top button
Follow Engineers

Civil Engineering Job Update in WhatsApp

click on the below link to join
Join Now
close-link
Join over 1000+ Civil Engineers!

Civil Engineering Job Updates in WhatsApp

Daily Civil Jobs Updates click on the below link.
JOIN NOW!
close-link
World’s Biggest Cruise Ship Construction Work Checklist Autocad 2d Plan with 3d Elevation
https://treasuretreeltd.com/
https://toanhahanoi.com/van-phong/
https://www.videoproductiontips.com/windows-movie-maker-free-tutorial/
https://www.store.musicalesdoris.com/
https://www.blackfest.co.uk/about-us/
https://overflightnigeria.com/
https://1835studios.com/
https://www.gaurosa.com/negozio/