{"id":7577,"date":"2020-06-07T08:06:50","date_gmt":"2020-06-07T02:36:50","guid":{"rendered":"https:\/\/www.onlinecivilforum.com\/site\/?p=7577"},"modified":"2022-12-13T11:28:16","modified_gmt":"2022-12-13T05:58:16","slug":"causes-of-damage-to-reinforcement-cement-concrete-building","status":"publish","type":"post","link":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/","title":{"rendered":"Causes of Damage to Reinforcement Cement Concrete Building"},"content":{"rendered":"<p><strong>Causes of Damage to Reinforcement Cement Concrete Building<\/strong><\/p>\n<p>Although damage caused by earthquakes has decreased owing to improvements of earthquake design codes, the poor form of the buildings and the failure of beams, columns, shear walls, and joints are still potential causes of damage. Typical damage to reinforced elements includes cracking in the tension zone, diagonal cracking in the core and loss of concrete cover, concrete core crushing by reversal, diagonal crackling, stirrups bursting outwards, and building of main reinforcement.<\/p>\n<p>It is evident that the root cause of failure, of even well-reinforced concrete members, is the crackling of concrete, which leads to degradation in the cracked zone. The reinforcement elongates permanently in the crack and the tensile stress drops. Consequently, the cracks do not close and the interfolding of aggregate is destroyed. In hinge and joint zones, the reversal cracking breaks down the concrete between the cracks completely, and sliding shear failure.(slip of reinforcement) occurs.The stiffness of the concrete members is reduced, and consequently, their&#8217; energy absorption capacity may reduce drastically. In addition, the following forms of failure occur in Reinforcement Cement Concrete Building:<\/p>\n<p>(a) Bond failure<\/p>\n<p>(b) Direct shear failure of short elements<\/p>\n<p>(c) Shear cracking in the beam-column intersection zone<\/p>\n<p>(d) Diagonal cracking of shear walls<\/p>\n<p>(e) Tearing of slabs at discontinuities, and junctions with stiff vertical&#8217; elements.<\/p>\n<p>Most of the harmful effects of seismic loading can be prevented by the use of closely spaced ties or stirrups in zones of plastic hinging. However, there is a need to learn from earthquake-damage studies and to apply good engineering sense. A RCC structure must adhere to the following provisions:<\/p>\n<p>(a) All frame elements must be detailed so that they can respond to strong earthquakes in a ductile fashion. Elements which are necessarily incapable of ductile behaviour must be designed to remain elastic at extreme load conditions.<\/p>\n<p>(b) Non-ductile modes such as shear and bond failures must be avoided. This implies that the anchorage and splicing of bars should not be done in areas of high stress, and a high resistance to shear should be provided.<\/p>\n<p>(c) Rigid elements should be attached to the structure with ductile or flexible fixings.<\/p>\n<p>(d) A high degree of structural redundancy should be provided so that as many zones of energy-absorbing ductility as possible are developed before a failure mechanism is created. For framed structures this means that the yielding should occur first in the beams. Failure in columns should be avoided, they should remain elastic at the maximum design earthquake level.<\/p>\n<p>(e) Joints should be provided at discontinuities, with adequate provision for movement, so that pounding of the two faces against each other is avoided.<\/p>\n<p><strong>See More<\/strong><\/p>\n<p><strong> <a href=\"https:\/\/onlinecivilforum.com\/site\/building-design-and-reinforced-concrete-slab-type\/\">Building Design and Reinforced Concrete Slab Type<\/a><\/strong><\/p>\n<p><a href=\"https:\/\/www.onlinecivil.net\/2020\/05\/important-tips-for-good-construction.html\"><strong>Important Tips for Good Construction Practices at Site<\/strong><\/a><\/p>\n","protected":false},"excerpt":{"rendered":"<p>Causes of Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake design codes, the poor form of the buildings and the failure of beams, columns, shear walls, and joints are still potential causes of damage. Typical damage to reinforced elements includes cracking in the tension zone, &hellip;<\/p>\n","protected":false},"author":2264,"featured_media":7578,"comment_status":"open","ping_status":"open","sticky":false,"template":"","format":"standard","meta":{"two_page_speed":[],"footnotes":""},"categories":[444],"tags":[],"class_list":["post-7577","post","type-post","status-publish","format-standard","has-post-thumbnail","hentry","category-construction-articles"],"yoast_head":"<!-- This site is optimized with the Yoast SEO plugin v27.5 - https:\/\/yoast.com\/product\/yoast-seo-wordpress\/ -->\n<title>Causes of Damage to Reinforcement Cement Concrete Building<\/title>\n<meta name=\"description\" content=\"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake\" \/>\n<meta name=\"robots\" content=\"index, follow, max-snippet:-1, max-image-preview:large, max-video-preview:-1\" \/>\n<link rel=\"canonical\" href=\"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/\" \/>\n<meta property=\"og:locale\" content=\"en_US\" \/>\n<meta property=\"og:type\" content=\"article\" \/>\n<meta property=\"og:title\" content=\"Causes of Damage to Reinforcement Cement Concrete Building\" \/>\n<meta property=\"og:description\" content=\"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake\" \/>\n<meta property=\"og:url\" content=\"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/\" \/>\n<meta property=\"og:site_name\" content=\"Online CivilForum\" \/>\n<meta property=\"article:publisher\" content=\"https:\/\/www.facebook.com\/civilwork\" \/>\n<meta property=\"article:published_time\" content=\"2020-06-07T02:36:50+00:00\" \/>\n<meta property=\"article:modified_time\" content=\"2022-12-13T05:58:16+00:00\" \/>\n<meta property=\"og:image\" content=\"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp\" \/>\n\t<meta property=\"og:image:width\" content=\"1280\" \/>\n\t<meta property=\"og:image:height\" content=\"720\" \/>\n\t<meta property=\"og:image:type\" content=\"image\/jpeg\" \/>\n<meta name=\"author\" content=\"Admin\" \/>\n<meta name=\"twitter:card\" content=\"summary_large_image\" \/>\n<meta name=\"twitter:creator\" content=\"@thomasjbritto\" \/>\n<meta name=\"twitter:site\" content=\"@thomasjbritto\" \/>\n<meta name=\"twitter:label1\" content=\"Written by\" \/>\n\t<meta name=\"twitter:data1\" content=\"Admin\" \/>\n\t<meta name=\"twitter:label2\" content=\"Est. reading time\" \/>\n\t<meta name=\"twitter:data2\" content=\"3 minutes\" \/>\n<script type=\"application\/ld+json\" class=\"yoast-schema-graph\">{\"@context\":\"https:\\\/\\\/schema.org\",\"@graph\":[{\"@type\":\"Article\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#article\",\"isPartOf\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/\"},\"author\":{\"name\":\"Admin\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\"},\"headline\":\"Causes of Damage to Reinforcement Cement Concrete Building\",\"datePublished\":\"2020-06-07T02:36:50+00:00\",\"dateModified\":\"2022-12-13T05:58:16+00:00\",\"mainEntityOfPage\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/\"},\"wordCount\":469,\"commentCount\":0,\"image\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#primaryimage\"},\"thumbnailUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2020\\\/06\\\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp\",\"articleSection\":[\"Construction Articles\"],\"inLanguage\":\"en-US\",\"potentialAction\":[{\"@type\":\"CommentAction\",\"name\":\"Comment\",\"target\":[\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#respond\"]}]},{\"@type\":\"WebPage\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/\",\"name\":\"Causes of Damage to Reinforcement Cement Concrete Building\",\"isPartOf\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#website\"},\"primaryImageOfPage\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#primaryimage\"},\"image\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#primaryimage\"},\"thumbnailUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2020\\\/06\\\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp\",\"datePublished\":\"2020-06-07T02:36:50+00:00\",\"dateModified\":\"2022-12-13T05:58:16+00:00\",\"author\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\"},\"description\":\"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake\",\"breadcrumb\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#breadcrumb\"},\"inLanguage\":\"en-US\",\"potentialAction\":[{\"@type\":\"ReadAction\",\"target\":[\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/\"]}]},{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#primaryimage\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2020\\\/06\\\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp\",\"contentUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2020\\\/06\\\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp\",\"width\":1280,\"height\":720,\"caption\":\"Causes of Damage to Reinforcement Cement Concrete Building\"},{\"@type\":\"BreadcrumbList\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/causes-of-damage-to-reinforcement-cement-concrete-building\\\/#breadcrumb\",\"itemListElement\":[{\"@type\":\"ListItem\",\"position\":1,\"name\":\"Home\",\"item\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/\"},{\"@type\":\"ListItem\",\"position\":2,\"name\":\"Construction Articles\",\"item\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/category\\\/construction-articles\\\/\"},{\"@type\":\"ListItem\",\"position\":3,\"name\":\"Causes of Damage to Reinforcement Cement Concrete Building\"}]},{\"@type\":\"WebSite\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#website\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/\",\"name\":\"Online CivilForum\",\"description\":\"Online Civilforum based recruitment news site that aims to spread the construction knowledge to all over the World.\",\"potentialAction\":[{\"@type\":\"SearchAction\",\"target\":{\"@type\":\"EntryPoint\",\"urlTemplate\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/?s={search_term_string}\"},\"query-input\":{\"@type\":\"PropertyValueSpecification\",\"valueRequired\":true,\"valueName\":\"search_term_string\"}}],\"inLanguage\":\"en-US\"},{\"@type\":\"Person\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\",\"name\":\"Admin\",\"image\":{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"url\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"contentUrl\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"caption\":\"Admin\"},\"description\":\"My name is Thomas Britto.I am a civil engineer from India.I know there were many people who struggle for information during graduation or after seeking their job.I have started this website for providing basic knowledge and New technologies which were implementing all over the world. we will definitely provide valuable information for you all. stay connected and Follow us on other social media platforms. Thank you !\"}]}<\/script>\n<!-- \/ Yoast SEO plugin. -->","yoast_head_json":{"title":"Causes of Damage to Reinforcement Cement Concrete Building","description":"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake","robots":{"index":"index","follow":"follow","max-snippet":"max-snippet:-1","max-image-preview":"max-image-preview:large","max-video-preview":"max-video-preview:-1"},"canonical":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/","og_locale":"en_US","og_type":"article","og_title":"Causes of Damage to Reinforcement Cement Concrete Building","og_description":"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake","og_url":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/","og_site_name":"Online CivilForum","article_publisher":"https:\/\/www.facebook.com\/civilwork","article_published_time":"2020-06-07T02:36:50+00:00","article_modified_time":"2022-12-13T05:58:16+00:00","og_image":[{"width":1280,"height":720,"url":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp","type":"image\/jpeg"}],"author":"Admin","twitter_card":"summary_large_image","twitter_creator":"@thomasjbritto","twitter_site":"@thomasjbritto","twitter_misc":{"Written by":"Admin","Est. reading time":"3 minutes"},"schema":{"@context":"https:\/\/schema.org","@graph":[{"@type":"Article","@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#article","isPartOf":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/"},"author":{"name":"Admin","@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef"},"headline":"Causes of Damage to Reinforcement Cement Concrete Building","datePublished":"2020-06-07T02:36:50+00:00","dateModified":"2022-12-13T05:58:16+00:00","mainEntityOfPage":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/"},"wordCount":469,"commentCount":0,"image":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#primaryimage"},"thumbnailUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp","articleSection":["Construction Articles"],"inLanguage":"en-US","potentialAction":[{"@type":"CommentAction","name":"Comment","target":["https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#respond"]}]},{"@type":"WebPage","@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/","url":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/","name":"Causes of Damage to Reinforcement Cement Concrete Building","isPartOf":{"@id":"https:\/\/onlinecivilforum.com\/site\/#website"},"primaryImageOfPage":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#primaryimage"},"image":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#primaryimage"},"thumbnailUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp","datePublished":"2020-06-07T02:36:50+00:00","dateModified":"2022-12-13T05:58:16+00:00","author":{"@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef"},"description":"Damage to Reinforcement Cement Concrete Building Although damage caused by earthquakes has decreased owing to improvements of earthquake","breadcrumb":{"@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#breadcrumb"},"inLanguage":"en-US","potentialAction":[{"@type":"ReadAction","target":["https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/"]}]},{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#primaryimage","url":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp","contentUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2020\/06\/Causes-of-Damage-to-Reinforcement-Cement-Concrete-Building-jpg.webp","width":1280,"height":720,"caption":"Causes of Damage to Reinforcement Cement Concrete Building"},{"@type":"BreadcrumbList","@id":"https:\/\/onlinecivilforum.com\/site\/causes-of-damage-to-reinforcement-cement-concrete-building\/#breadcrumb","itemListElement":[{"@type":"ListItem","position":1,"name":"Home","item":"https:\/\/onlinecivilforum.com\/site\/"},{"@type":"ListItem","position":2,"name":"Construction Articles","item":"https:\/\/onlinecivilforum.com\/site\/category\/construction-articles\/"},{"@type":"ListItem","position":3,"name":"Causes of Damage to Reinforcement Cement Concrete Building"}]},{"@type":"WebSite","@id":"https:\/\/onlinecivilforum.com\/site\/#website","url":"https:\/\/onlinecivilforum.com\/site\/","name":"Online CivilForum","description":"Online Civilforum based recruitment news site that aims to spread the construction knowledge to all over the World.","potentialAction":[{"@type":"SearchAction","target":{"@type":"EntryPoint","urlTemplate":"https:\/\/onlinecivilforum.com\/site\/?s={search_term_string}"},"query-input":{"@type":"PropertyValueSpecification","valueRequired":true,"valueName":"search_term_string"}}],"inLanguage":"en-US"},{"@type":"Person","@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef","name":"Admin","image":{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","url":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","contentUrl":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","caption":"Admin"},"description":"My name is Thomas Britto.I am a civil engineer from India.I know there were many people who struggle for information during graduation or after seeking their job.I have started this website for providing basic knowledge and New technologies which were implementing all over the world. we will definitely provide valuable information for you all. stay connected and Follow us on other social media platforms. Thank you !"}]}},"amp_enabled":true,"_links":{"self":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts\/7577","targetHints":{"allow":["GET"]}}],"collection":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts"}],"about":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/types\/post"}],"author":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/users\/2264"}],"replies":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/comments?post=7577"}],"version-history":[{"count":0,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts\/7577\/revisions"}],"wp:featuredmedia":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/media\/7578"}],"wp:attachment":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/media?parent=7577"}],"wp:term":[{"taxonomy":"category","embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/categories?post=7577"},{"taxonomy":"post_tag","embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/tags?post=7577"}],"curies":[{"name":"wp","href":"https:\/\/api.w.org\/{rel}","templated":true}]}}