{"id":772,"date":"2016-09-30T11:43:04","date_gmt":"2016-09-30T06:13:04","guid":{"rendered":"http:\/\/onlinecivilforum.com\/site\/?p=772"},"modified":"2022-12-13T11:52:40","modified_gmt":"2022-12-13T06:22:40","slug":"one-way-slab-reinforcement-details","status":"publish","type":"post","link":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/","title":{"rendered":"One way slab Reinforcement Details"},"content":{"rendered":"<p class=\"qtext_para\">One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one, the slab will be one way.<\/p>\n<p class=\"qtext_para\">Now in one way Slab as one side is bigger than the other side most of the load is carried by that side only so providing main reinforcement corresponding to that load carrying side will be sufficient. So to support that larger side <b>Main Reinforcement is provided perpendicular to that side or parallel to shorter side and along longer side(I.e. parallel) only steel required for supporting is provided called distribution steel <\/b>which will not help in carrying any load.<\/p>\n<p class=\"qtext_para\">Main steel will be calculated by formula for limit state design formula which is derived by equating compressive and tensile forces which is-<\/p>\n<p class=\"qtext_para\">Ast = 0.5Fck\/Fu{1-\u221a1\u20132.6Mu\/Fck.<wbr>b.d}b.d<\/p>\n<p class=\"qtext_para\">and Distribution Steel is calculated as-<\/p>\n<p class=\"qtext_para\">0.15% of Ag for mild steel.<\/p>\n<p class=\"qtext_para\">0.12% of Ag for tor steel.<\/p>\n<p class=\"qtext_para\">Where,Ast=area of steel in tension<\/p>\n<p class=\"qtext_para\">Fck= Characteristic strength for grade of concrete used.<\/p>\n<p class=\"qtext_para\">Fu=Ultimate strength of steel used.<\/p>\n<p class=\"qtext_para\">Mu=Ultimate moment resisted<\/p>\n<p class=\"qtext_para\">b=breadth of the section<\/p>\n<p class=\"qtext_para\">d=depth of the section<\/p>\n<p class=\"qtext_para\">Ag=Gross area for the section.<\/p>\n","protected":false},"excerpt":{"rendered":"<p>One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one, the slab will be one way. Now in one way Slab as one side is bigger than the other side most of the load is carried &hellip;<\/p>\n","protected":false},"author":2264,"featured_media":561,"comment_status":"open","ping_status":"open","sticky":false,"template":"","format":"standard","meta":{"two_page_speed":[],"footnotes":""},"categories":[50],"tags":[65,164,102],"class_list":["post-772","post","type-post","status-publish","format-standard","has-post-thumbnail","hentry","category-reinforcement","tag-reinforcement","tag-slab-design","tag-structural-design"],"yoast_head":"<!-- This site is optimized with the Yoast SEO plugin v27.3 - https:\/\/yoast.com\/product\/yoast-seo-wordpress\/ -->\n<title>One way slab Reinforcement Details<\/title>\n<meta name=\"description\" content=\"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one\" \/>\n<meta name=\"robots\" content=\"index, follow, max-snippet:-1, max-image-preview:large, max-video-preview:-1\" \/>\n<link rel=\"canonical\" href=\"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/\" \/>\n<meta property=\"og:locale\" content=\"en_US\" \/>\n<meta property=\"og:type\" content=\"article\" \/>\n<meta property=\"og:title\" content=\"One way slab Reinforcement Details\" \/>\n<meta property=\"og:description\" content=\"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one\" \/>\n<meta property=\"og:url\" content=\"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/\" \/>\n<meta property=\"og:site_name\" content=\"Online CivilForum\" \/>\n<meta property=\"article:publisher\" content=\"https:\/\/www.facebook.com\/civilwork\" \/>\n<meta property=\"article:published_time\" content=\"2016-09-30T06:13:04+00:00\" \/>\n<meta property=\"article:modified_time\" content=\"2022-12-13T06:22:40+00:00\" \/>\n<meta property=\"og:image\" content=\"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif\" \/>\n\t<meta property=\"og:image:width\" content=\"572\" \/>\n\t<meta property=\"og:image:height\" content=\"426\" \/>\n\t<meta property=\"og:image:type\" content=\"image\/gif\" \/>\n<meta name=\"author\" content=\"Admin\" \/>\n<meta name=\"twitter:card\" content=\"summary_large_image\" \/>\n<meta name=\"twitter:creator\" content=\"@thomasjbritto\" \/>\n<meta name=\"twitter:site\" content=\"@thomasjbritto\" \/>\n<meta name=\"twitter:label1\" content=\"Written by\" \/>\n\t<meta name=\"twitter:data1\" content=\"Admin\" \/>\n\t<meta name=\"twitter:label2\" content=\"Est. reading time\" \/>\n\t<meta name=\"twitter:data2\" content=\"1 minute\" \/>\n<script type=\"application\/ld+json\" class=\"yoast-schema-graph\">{\"@context\":\"https:\\\/\\\/schema.org\",\"@graph\":[{\"@type\":\"Article\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#article\",\"isPartOf\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/\"},\"author\":{\"name\":\"Admin\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\"},\"headline\":\"One way slab Reinforcement Details\",\"datePublished\":\"2016-09-30T06:13:04+00:00\",\"dateModified\":\"2022-12-13T06:22:40+00:00\",\"mainEntityOfPage\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/\"},\"wordCount\":211,\"commentCount\":3,\"image\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#primaryimage\"},\"thumbnailUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2016\\\/09\\\/One-way-slab.gif\",\"keywords\":[\"Reinforcement\",\"Slab Design\",\"Structural Design\"],\"articleSection\":[\"Reinforcement\"],\"inLanguage\":\"en-US\",\"potentialAction\":[{\"@type\":\"CommentAction\",\"name\":\"Comment\",\"target\":[\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#respond\"]}]},{\"@type\":\"WebPage\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/\",\"name\":\"One way slab Reinforcement Details\",\"isPartOf\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#website\"},\"primaryImageOfPage\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#primaryimage\"},\"image\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#primaryimage\"},\"thumbnailUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2016\\\/09\\\/One-way-slab.gif\",\"datePublished\":\"2016-09-30T06:13:04+00:00\",\"dateModified\":\"2022-12-13T06:22:40+00:00\",\"author\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\"},\"description\":\"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one\",\"breadcrumb\":{\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#breadcrumb\"},\"inLanguage\":\"en-US\",\"potentialAction\":[{\"@type\":\"ReadAction\",\"target\":[\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/\"]}]},{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#primaryimage\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2016\\\/09\\\/One-way-slab.gif\",\"contentUrl\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/wp-content\\\/uploads\\\/2016\\\/09\\\/One-way-slab.gif\",\"width\":572,\"height\":426},{\"@type\":\"BreadcrumbList\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/one-way-slab-reinforcement-details\\\/#breadcrumb\",\"itemListElement\":[{\"@type\":\"ListItem\",\"position\":1,\"name\":\"Home\",\"item\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/\"},{\"@type\":\"ListItem\",\"position\":2,\"name\":\"Gendral Civil Engineering\",\"item\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/category\\\/gendral-civil-engineering\\\/\"},{\"@type\":\"ListItem\",\"position\":3,\"name\":\"Reinforcement\",\"item\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/category\\\/gendral-civil-engineering\\\/reinforcement\\\/\"},{\"@type\":\"ListItem\",\"position\":4,\"name\":\"One way slab Reinforcement Details\"}]},{\"@type\":\"WebSite\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#website\",\"url\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/\",\"name\":\"Online CivilForum\",\"description\":\"Online Civilforum based recruitment news site that aims to spread the construction knowledge to all over the World.\",\"potentialAction\":[{\"@type\":\"SearchAction\",\"target\":{\"@type\":\"EntryPoint\",\"urlTemplate\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/?s={search_term_string}\"},\"query-input\":{\"@type\":\"PropertyValueSpecification\",\"valueRequired\":true,\"valueName\":\"search_term_string\"}}],\"inLanguage\":\"en-US\"},{\"@type\":\"Person\",\"@id\":\"https:\\\/\\\/onlinecivilforum.com\\\/site\\\/#\\\/schema\\\/person\\\/ccbccea3895033bfa0aa3bc0683d83ef\",\"name\":\"Admin\",\"image\":{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"url\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"contentUrl\":\"https:\\\/\\\/secure.gravatar.com\\\/avatar\\\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g\",\"caption\":\"Admin\"},\"description\":\"My name is Thomas Britto.I am a civil engineer from India.I know there were many people who struggle for information during graduation or after seeking their job.I have started this website for providing basic knowledge and New technologies which were implementing all over the world. we will definitely provide valuable information for you all. stay connected and Follow us on other social media platforms. Thank you !\"}]}<\/script>\n<!-- \/ Yoast SEO plugin. -->","yoast_head_json":{"title":"One way slab Reinforcement Details","description":"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one","robots":{"index":"index","follow":"follow","max-snippet":"max-snippet:-1","max-image-preview":"max-image-preview:large","max-video-preview":"max-video-preview:-1"},"canonical":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/","og_locale":"en_US","og_type":"article","og_title":"One way slab Reinforcement Details","og_description":"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one","og_url":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/","og_site_name":"Online CivilForum","article_publisher":"https:\/\/www.facebook.com\/civilwork","article_published_time":"2016-09-30T06:13:04+00:00","article_modified_time":"2022-12-13T06:22:40+00:00","og_image":[{"width":572,"height":426,"url":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif","type":"image\/gif"}],"author":"Admin","twitter_card":"summary_large_image","twitter_creator":"@thomasjbritto","twitter_site":"@thomasjbritto","twitter_misc":{"Written by":"Admin","Est. reading time":"1 minute"},"schema":{"@context":"https:\/\/schema.org","@graph":[{"@type":"Article","@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#article","isPartOf":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/"},"author":{"name":"Admin","@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef"},"headline":"One way slab Reinforcement Details","datePublished":"2016-09-30T06:13:04+00:00","dateModified":"2022-12-13T06:22:40+00:00","mainEntityOfPage":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/"},"wordCount":211,"commentCount":3,"image":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#primaryimage"},"thumbnailUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif","keywords":["Reinforcement","Slab Design","Structural Design"],"articleSection":["Reinforcement"],"inLanguage":"en-US","potentialAction":[{"@type":"CommentAction","name":"Comment","target":["https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#respond"]}]},{"@type":"WebPage","@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/","url":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/","name":"One way slab Reinforcement Details","isPartOf":{"@id":"https:\/\/onlinecivilforum.com\/site\/#website"},"primaryImageOfPage":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#primaryimage"},"image":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#primaryimage"},"thumbnailUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif","datePublished":"2016-09-30T06:13:04+00:00","dateModified":"2022-12-13T06:22:40+00:00","author":{"@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef"},"description":"One way Slab are slab in which one side is very large compared to the other one. Generally if one side is more than double of the other one","breadcrumb":{"@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#breadcrumb"},"inLanguage":"en-US","potentialAction":[{"@type":"ReadAction","target":["https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/"]}]},{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#primaryimage","url":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif","contentUrl":"https:\/\/onlinecivilforum.com\/site\/wp-content\/uploads\/2016\/09\/One-way-slab.gif","width":572,"height":426},{"@type":"BreadcrumbList","@id":"https:\/\/onlinecivilforum.com\/site\/one-way-slab-reinforcement-details\/#breadcrumb","itemListElement":[{"@type":"ListItem","position":1,"name":"Home","item":"https:\/\/onlinecivilforum.com\/site\/"},{"@type":"ListItem","position":2,"name":"Gendral Civil Engineering","item":"https:\/\/onlinecivilforum.com\/site\/category\/gendral-civil-engineering\/"},{"@type":"ListItem","position":3,"name":"Reinforcement","item":"https:\/\/onlinecivilforum.com\/site\/category\/gendral-civil-engineering\/reinforcement\/"},{"@type":"ListItem","position":4,"name":"One way slab Reinforcement Details"}]},{"@type":"WebSite","@id":"https:\/\/onlinecivilforum.com\/site\/#website","url":"https:\/\/onlinecivilforum.com\/site\/","name":"Online CivilForum","description":"Online Civilforum based recruitment news site that aims to spread the construction knowledge to all over the World.","potentialAction":[{"@type":"SearchAction","target":{"@type":"EntryPoint","urlTemplate":"https:\/\/onlinecivilforum.com\/site\/?s={search_term_string}"},"query-input":{"@type":"PropertyValueSpecification","valueRequired":true,"valueName":"search_term_string"}}],"inLanguage":"en-US"},{"@type":"Person","@id":"https:\/\/onlinecivilforum.com\/site\/#\/schema\/person\/ccbccea3895033bfa0aa3bc0683d83ef","name":"Admin","image":{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","url":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","contentUrl":"https:\/\/secure.gravatar.com\/avatar\/cdf45ee29d77ef3d29bfff6e0c7a02774edc163b7d650db08ea7ffabd5deffba?s=96&r=g","caption":"Admin"},"description":"My name is Thomas Britto.I am a civil engineer from India.I know there were many people who struggle for information during graduation or after seeking their job.I have started this website for providing basic knowledge and New technologies which were implementing all over the world. we will definitely provide valuable information for you all. stay connected and Follow us on other social media platforms. Thank you !"}]}},"amp_enabled":true,"_links":{"self":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts\/772","targetHints":{"allow":["GET"]}}],"collection":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts"}],"about":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/types\/post"}],"author":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/users\/2264"}],"replies":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/comments?post=772"}],"version-history":[{"count":0,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/posts\/772\/revisions"}],"wp:featuredmedia":[{"embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/media\/561"}],"wp:attachment":[{"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/media?parent=772"}],"wp:term":[{"taxonomy":"category","embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/categories?post=772"},{"taxonomy":"post_tag","embeddable":true,"href":"https:\/\/onlinecivilforum.com\/site\/wp-json\/wp\/v2\/tags?post=772"}],"curies":[{"name":"wp","href":"https:\/\/api.w.org\/{rel}","templated":true}]}}